You can add these yourself.
I can tell you where if you post a picture.
Wall Mart has r134a.
You will need a hose adapter but these can be made easily.
I looked up Supco Piercing Valve and interestingly, there's more than one. There's the Supco Bullet Piercing Valve, Silver; and the Supco BPV31. Both really cheap.
Next time I can sit down and fiddle, I'm going to pull the covers off the cooling unit and take some pictures.
Hate to ask a silly question but does the compressor run.
This is sounding less like something I should do myself, and more like something I should give to an HVAC guy to fix.
Based on you post about charging.
It may be over charged the amps listed are usually higher than reality operation.
You compressor may be opening it's internal limit. Verify with amp draw. Could also be high pressure lock out. This would equalize quickly once stopped. What kind of compressor?
Your previous comments and human nature would have me exploring over charged.
Add till the suction line just starts to sweet be little at a time.
Beer can cold.
Most units run at about 2/3 listed amps. If I see one drawing listed amps I give my, time to label a coffee can New A/C fund.
Tell me about the water your sitting in, what's the inside of the water coil look like. Can you bypass it and run a demineralizing solution through it.